Metadata-Version: 2.4
Name: heatpumpmodel
Version: 0.5.0
Summary: Heat-pump seasonal-performance model (Rogeau et al. 2024) shared by buildingmodel and building_eload
Author-email: Yassine Abdelouadoud <yassine.abdelouadoud@gmail.com>
Maintainer-email: Yassine Abdelouadoud <yassine.abdelouadoud@gmail.com>
License: The MIT License (MIT)
        =====================
        
        - Copyright © `2025` `Yoann Chiche`
        - Copyright © `2025` `Seddik Yassine Abdelouadoud`
        - Copyright © `2025` `Anna Cocchi`
        
        Permission is hereby granted, free of charge, to any person
        obtaining a copy of this software and associated documentation
        files (the “Software”), to deal in the Software without
        restriction, including without limitation the rights to use,
        copy, modify, merge, publish, distribute, sublicense, and/or sell
        copies of the Software, and to permit persons to whom the
        Software is furnished to do so, subject to the following
        conditions:
        
        The above copyright notice and this permission notice shall be
        included in all copies or substantial portions of the Software.
        
        THE SOFTWARE IS PROVIDED “AS IS”, WITHOUT WARRANTY OF ANY KIND,
        EXPRESS OR IMPLIED, INCLUDING BUT NOT LIMITED TO THE WARRANTIES
        OF MERCHANTABILITY, FITNESS FOR A PARTICULAR PURPOSE AND
        NONINFRINGEMENT. IN NO EVENT SHALL THE AUTHORS OR COPYRIGHT
        HOLDERS BE LIABLE FOR ANY CLAIM, DAMAGES OR OTHER LIABILITY,
        WHETHER IN AN ACTION OF CONTRACT, TORT OR OTHERWISE, ARISING
        FROM, OUT OF OR IN CONNECTION WITH THE SOFTWARE OR THE USE OR
        OTHER DEALINGS IN THE SOFTWARE.
        
Classifier: Development Status :: 3 - Alpha
Classifier: License :: OSI Approved :: MIT License
Classifier: Operating System :: MacOS :: MacOS X
Classifier: Operating System :: Microsoft :: Windows
Classifier: Operating System :: POSIX :: Linux
Classifier: Programming Language :: Python :: 3.10
Classifier: Programming Language :: Python :: 3.11
Classifier: Programming Language :: Python :: 3.12
Classifier: Programming Language :: Python :: 3.13
Classifier: Topic :: Scientific/Engineering :: Physics
Requires-Python: <4.0.0,>=3.8
Description-Content-Type: text/markdown
License-File: LICENSE
Requires-Dist: numpy
Provides-Extra: dev
Requires-Dist: pytest; extra == "dev"
Requires-Dist: pytest-cov; extra == "dev"
Requires-Dist: ruff>=0.16; extra == "dev"
Dynamic: license-file

# heatpumpmodel

Single-source implementation of the steady-state (bin-style) heat-pump performance
model of

> A. Rogeau, R. Vieubled, M. de la Ruche, G. Girard, *"A generic methodology for
> mapping the performance of various heat pump configurations considering part-load
> behavior"*, Energy and Buildings 2024,
> <https://doi.org/10.1016/j.enbuild.2024.114471>

`numpy` is the only dependency. The package holds **physics only**: it knows nothing
about a building stock, a weather reader or a simulation pipeline. Callers pass hourly
arrays in and keep their own integration layer.

It exists so that [`buildingmodel`](https://gitlab.com/energytransition/buildingmodel)
and `building_eload` share one copy of the physics instead of two that drift apart
(buildingmodel issue #47).

## Install

```bash
pip install heatpumpmodel
# or, from a checkout:
pip install -e ".[dev]"
```

## Use

```python
import numpy as np
from heatpumpmodel import (
    Emitter, HeatPumpConfig, Mode, System, Technology,
    compute_T_base, hourly_power_split, scop, size_heat_pump,
)

# hourly series over a year: outdoor temperature (°C), relative humidity (%),
# and heat demand in any single consistent unit (it cancels in every ratio).
t_out = ...
rh = ...
demand = np.clip(20.0 - t_out, 0.0, None)

cfg = HeatPumpConfig(System.A_W, Mode.M, Emitter.MT, Technology.ON_OFF)
sizing = size_heat_pump(cfg, demand, t_out, compute_T_base(t_out))
p_h, p_e, p_h_backup = hourly_power_split(cfg, sizing, demand, t_out, rh=rh)

print(scop(p_h, p_e))            # seasonal COP
```

`seasonal_performance(cfg, sizing, demand, t_out, rh=rh)` bundles
`{"scop", "ecr", "peak_share"}` in one call.

### Configuration axes

| Axis | Values |
|---|---|
| `System` | `A_A` (air/air), `A_W` (air/water), `G_W` (ground/water) |
| `Mode` | `M`, `M_SB`, `BA` (bivalent alternative), `BP` (bivalent parallel) |
| `Emitter` | `FH` 35 °C, `LT` 45 °C, `MT` 55 °C, `HT` 65 °C, `FAN_COIL` (sink = indoor setpoint; direct expansion only) |
| `Technology` | `ON_OFF`, `BI_COMPRESSOR`, `INVERTER` |

Sub-models (`COPCurve`, `TwoBranchCOPCurve`, `DefrostModel`, `PartLoadModel`,
`WeatherCompensation`) are dataclasses on `HeatPumpConfig` and can be replaced with
manufacturer-specific fits.

### The A/W COP curve (behavioural break in 0.3.0)

The default **A/W** full-load curve is `TwoBranchCOPCurve`: a defrost-degraded branch
(`5.60 − 0.09·ΔT + 0.0005·ΔT²`, `T_ext ≤ −3 °C`) and a frost-free branch
(`9.302 − 0.223·ΔT + 0.0017·ΔT²`, `T_ext ≥ +6 °C`), linearly interpolated in the
outdoor-air temperature between the two. Before 0.3.0 only the degraded branch existed,
applied at every outdoor temperature — the collapsed form of the source's Eq. (3.8) that
the authors' published code produces. **A/W SCOP therefore rises** — 4.4 % to 19.5 % across
the emitter × technology × mode grid on a synthetic Paris-like year, most in mild weather;
A/A and G/W are unaffected.

Because `heating_capacity` (Eq. 6) reads the same curve, it is a **capacity** change too:
for A/W, M mode, floor heating, inverter on that year, capacity at `T_so = +10 °C` is
**+31 %**, mean capacity over heating hours **+22 %**, hours below minimum modulation go
843 → 1402, `T_biv2` 11.8 → 9.7 °C and `ECR` 81.1 → 89.7. `Q_nom`/`P_e_nom` are unchanged
in M / M+SB mode (their design point sits on the degraded branch for any `T_base ≤ −3 °C`)
but move slightly in BA/BP, whose backup bisection runs on the branch-aware capacity.

The best case of that grid (FH, inverter, BA) now reaches SCOP ≈ 4.67, at or above the top
class of the paper's own European map — headroom that follows from implementing the printed
source faithfully, not from any empirical validation. To reproduce pre-0.3.0 A/W numbers
(and to reproduce the paper's Fig. 4, which is an output of the collapsed curve):

```python
from heatpumpmodel import HeatPumpConfig, LEGACY_A_W_SINGLE_CURVE, System, Mode, Emitter, Technology

cfg = HeatPumpConfig(System.A_W, Mode.M, Emitter.MT, Technology.ON_OFF,
                     cop_curve=LEGACY_A_W_SINGLE_CURVE)
```

`TwoBranchCOPCurve.cop_fl` requires the source (outdoor-air) temperature and raises if it
is missing — so `COP_CURVES[System.A_W].cop_fl(dT)` without `t_so`, which used to return an
array, now raises. See its docstring in `heatpumpmodel/core.py` for the provenance chain
(PhD thesis tel-02969503, not Ruhnau et al.) and for the documented overlap between the
branch structure and `DefrostModel` — which also means an A/W-vs-A/A SCOP gap now straddles
two different defrost representations and partly reflects curve lineage, not physics.

### Check the sizing solve status on BA/BP

```python
sizing = size_heat_pump(cfg, demand, t_out, compute_T_base(t_out))
if not sizing.converged:                 # sizing.solve_status names which rail was hit
    ...                                  # surface it; do not publish a railed Q_nom
```

For `Mode.BA` / `Mode.BP`, `Q_nom` is solved by bisection for a 10 % backup share. When
that target is unreachable the solver returns a bracket rail (`4·h_base` or `1e-3·h_base`)
as a best-effort size, and every quantity derived from it is an artefact of the search
interval rather than a sizing. Since 0.3.0 `HeatPumpSizing.solve_status`
(`SizingSolveStatus.CONVERGED` / `RAILED_LOW` / `RAILED_HIGH`) and the derived
`converged` property make that visible.

**Since 0.4.0 a fourth status, `MAX_ITER`**, covers the bisection's third silent exit: the
target *was* bracketed but `|achieved − target|` never met the tolerance, and the final
midpoint is returned — the exit that looks most like a normal answer (interior value, no
rail, no exception). `converged` is `False` there. It is a reporting change only: on the committed
13 824-solve grid (`scripts/differential_sizing_status.py`, which regenerates these
numbers), 756 solves (all `BA`) reclassify and **no number moves**. The flip count and the
residual ceiling are properties of that grid — a different but equally defensible grid
moves both; what is grid-independent is the 0 numeric moves, the confinement to `BA`, and
residuals of the order of the solver's tolerance. Consumers wanting the old grouping test
`solve_status in (CONVERGED, MAX_ITER)`.
`converged` still means only "no rail and no `max_iter` exhaustion", and it is also the
default for the closed-form M / M+SB rule, so check `Q_nom` for plausibility as well.

### Declared capacity, and the backup-share target

```python
from heatpumpmodel import DeclaredCapacity, SizingBasis, compute_T_base, size_heat_pump

sizing = size_heat_pump(cfg, demand, t_out, compute_T_base(t_out),  # 8 kW at 55/7 °C
                        declared=DeclaredCapacity(8000.0, sink_c=55.0, source_c=7.0))
sizing.basis is SizingBasis.DECLARED     # T_biv / T_biv2 are NaN — see below
```

`declared` skips the sizing rule and uses the caller's capacity, rescaling `P_e_nom` and
`P_e_min` through the package's own Eq. 5 / Eq. 13 at the declared rating point. **The
rating point is required, not defaulted**: a declared thermal power is not automatically
`Q_nom` (G/W nameplates are rated at 0 °C source water — a different physical quantity
from an air-source rating). The bivalence diagnostics are properties of the derived solve,
so they are invalidated (`NaN`) rather than carried, and the choice is recorded on
`sizing.basis` (`DERIVED` by default; every existing call is unchanged). Neither
convention is endorsed here — on the ADEME campaign derived and declared arms err in
opposite directions on backup engagement and neither reproduces the metered value.

`size_heat_pump(..., backup_target=...)` promotes the solver's private default to the
public signature (validated to `(0, 1)`, fail-loud outside it). It defaults to `None`, the
sentinel for "no target was asked for", which takes the rule's own 0.10 convention —
**unchanged and bit-identical**. The 10 % share is a convention of the sizing rule, not a
prediction, and it has to be reachable by a caller comparing against measured data.
Passing `declared` together with **any** explicit `backup_target` raises, `0.10` included:
the caller asked for a target and the declared path could only ignore it.

### Meter-boundary layers: auxiliaries and DHW (0.4.0)

`heatpumpmodel.core` predicts *machine* electricity. What a dwelling's distribution board
draws is more than that (heatpumpmodel#5 §1.3):

```
E_total = E_compressor(COP*) + E_backup            <- core
        + E_aux(standby, circulators, source pump) <- heatpumpmodel.auxiliaries
        + E_DHW(charge conversion + boost)         <- heatpumpmodel.dhw
```

Both are **additive layers**: they report their own terms beside the core's, never folded
into them, and they move nothing the core computes — no space-heating COP, no capacity, no
sizing. A consumer that never calls them gets the same numbers byte for byte.

`auxiliaries` predicts the electricity *inside a declared metering perimeter*, and the
perimeter is a **derived output**, not a label the caller asserts: `plan_aux_terms` turns
three recorded installation facts (ground source? separate auxiliaries circuit? decoupling
bottle or buffer tank?) into the inclusion set and an `H4*` / `H4*-ext` / `H1*+bu` label.
A consumer wired *outside* the perimeter is suppressed, not added — an "auxiliaries"
breaker *reduces* the prediction, because the meter being predicted cannot see what is on
it. Results come back component-wise (standby, circulator, overlap deduction, source pump)
for three named literature coefficient cases; there is no default coefficient set.

`dhw` converts a DHW **charge-heat** series into the electricity the same compressor
spends making it: the same machine at a different operating point (scope A). DHW demand,
draw profiles and tank dynamics are scope B and are not modelled. The sink is the charge
temperature, passed explicitly, so the space-heating sink and the sizing solve cannot
move; the immersion boost is a measured pass-through, never a prediction.

Status, in the words that must travel with any number from these layers: the auxiliary
**circulator coefficient is an open question** — it runs +15 … +51 % above its own
campaign's same-sample energy anchor (criterion K13 **FAIL**), and it is reported, never
tuned. That comparison is measured on the campaign's **mild year**: R8 states a 2021-like
winter would cut SCOP by 15–20 %, and an auxiliary share of electricity is mechanically
higher in a mild year on *both* sides of an anchor comparison — so the vintage does not
explain the overshoot away, and equally nothing here generalises to a design winter. The
DHW layer is **prototyped and gated as a diagnostic, not validated** (the pre-registered
rule returns FAIL on the total clause), quotable only with its target's own 1.00–1.13×
one-directional fidelity, **measured on 4 dwellings**, in the same breath — and those four
are Δ ranks 24, 27, 31 and 34 of 34, i.e. an agreement on the high-Δ tail rather than on a
random four. On the pre-registered basis the informative subset is 1 pass (the strawman
clause) / 5 fail, and on the split basis 2 pass / 1 fail / 3 uninformative; it is never
"passes five of six". Read the two module docstrings
(`heatpumpmodel/auxiliaries.py`, `heatpumpmodel/dhw.py`) before publishing either: they
carry the provenance, the guards, the counted-flag semantics and the full status wording.

### From French DPE data

`heatpumpmodel.dpe` maps `buildingdata`'s `heat_pump_type` / `heating_emitter_type` /
`heat_pump_installation_period` DPE columns onto a `HeatPumpConfig`, so `buildingmodel`
and `building_eload` resolve the same building to the same machine in both the static and
dynamic stages instead of each guessing independently:

```python
from heatpumpmodel import HeatPumpConfig, System, Mode, Emitter, Technology, config_from_dpe

default = HeatPumpConfig(System.A_W, Mode.M, Emitter.MT, Technology.ON_OFF)
cfg = config_from_dpe("air/air", "air", "[2015, 2100]", default=default)
```

Any DPE column that is `None` falls back to the matching axis of `default`; a *present*
value outside the module's vocabulary raises `ValueError` rather than drifting silently.
See `heatpumpmodel/dpe.py` for the vocabulary vintage and the full mapping tables.

**The emitter is resolved against the system, not from `heating_emitter_type` alone.**
The DPE's `"air"` emission class is two different machines: on an air/air generator it is
direct expansion and the sink *is* the room (`FAN_COIL`), while on a hydronic generator it
is a fan-coil water loop — a *ventilo-convecteur*, still circulating water at roughly
35–45 °C — which resolves to `LT` (45 °C). The invariant is `FAN_COIL` ⇔ `A_A`. Before
0.5.0 `"air"` mapped to `FAN_COIL` unconditionally, sinking hydronic units to the indoor
setpoint and overstating their SCOP (up to 10.3 on ground-source records); that fix moves
the numbers for ~15 % of the DPE heat-pump stock, so a consumer upgrading from 0.4.x must
re-measure rather than bump the floor silently (heatpumpmodel#6).

The same invariant is enforced at the constructor: since 0.5.0
`HeatPumpConfig(System.A_W | System.G_W, ..., Emitter.FAN_COIL, ...)` raises `ValueError`
instead of silently sinking the machine to the indoor setpoint. Reach for `Emitter.LT` for
a hydronic fan-coil loop, or `System.A_A` if the unit really is direct expansion.

## Conventions

- Temperatures in °C, ΔT gaps in K.
- Powers/demand in one arbitrary, self-cancelling unit.
- Relative humidity in **percent [0, 100]** — the EPW convention.
- Air-source configs (`A/A`, `A/W`) **require** an `rh` series: a missing, all-NaN,
  all-zero or partially non-finite `rh`, a `[0, 1]` *fraction*-convention series, or any
  value outside `[0, 100]` raises `ValueError` rather than silently skipping the defrost
  derate (which would leave SCOP ~5 % optimistic). The checks are whole-series: one bad
  summer hour fails the call.
- Every effective COP is floored at 1.0 — a heat pump never draws more electricity
  than the resistance backup would for the same heat. The floor is exported as
  `HP_COP_FLOOR`, so layers and consumers test against it instead of mirroring the
  literal.

## Documentation

`doc/heat_pump_model_spec.md` is the implementation contract: equation-by-equation
mapping to the paper, coefficient provenance (including the values resolved from the
authors' Zenodo code rather than the PDF), and the documented deviations.

## Tests

```bash
pytest                          # hermetic suite, synthetic climate
HEATPUMPMODEL_PARIS_EPW=/path/to/paris.epw pytest -m integration
```

The integration test reproduces the paper's Fig. 4 SCOP values and needs the authors'
Paris-Montsouris TMY EPW; it skips when that file is not supplied. See its docstring
for why an ERA5 Paris record does not substitute.

## Licence

MIT — see `LICENSE`.